I wasn’t ever planning to but just wondered why? Are they just pushing the boat too much?
3-5
5-10
10-20 times and all that sparkery stuff
It takes a lot to trip a Type D, all MCBs can handle a surprising amount of continued overcurrent, so it is not a good idea to put in a D unless it is necessary.
I've had a nuisance trip on a C but that is very rare. Often a manufacturer will state if a Type C or D breaker is required.
One thing you can do which is sometimes handy - put in a 32A feed to a commando socket from a standard 32A type B breaker and then make up a breakout box (like the caravan hookup things) that plugs in with a couple of 16A type C breakers in and a couple of 16A sockets.
The advantage of this is it gives you two protected outlets and finding Type B breakers for an existing consumer unit is usually a lot easier. If you are not hammering both outlets at once the Type B should handle it.