Contactor 1 (on the left) feeds a 3 ph load, looks like a flexible four core with black wires. (9A on 3 phase is a fair load ...)
Contactor 2 (next one along) feeds the grey brown and black cable. both at the top of the box.
Contactor 3 just feeds two phases (415V) to something that has been disconnected, again at the top.
You wouldn't normally feed a burner with its own control system via an overload, unless the control for the burner is done at the same time.
You wouldn't run a burner on two phase either, so I dunno what was on those two. BTW, that 2 phase is on seperate mcb's, very naughty, if one trips you have the other phase all over the load as well as coming back into the panel. They should be grouped/linked or whatever its called.
Contactor 2 (next one along) feeds the grey brown and black cable. both at the top of the box.
Contactor 3 just feeds two phases (415V) to something that has been disconnected, again at the top.
You wouldn't normally feed a burner with its own control system via an overload, unless the control for the burner is done at the same time.
You wouldn't run a burner on two phase either, so I dunno what was on those two. BTW, that 2 phase is on seperate mcb's, very naughty, if one trips you have the other phase all over the load as well as coming back into the panel. They should be grouped/linked or whatever its called.