Except when it doesNo it won't include inrush current, it's maximum current it will draw in normal operation.
Inrush will be dealt with breaker type b, c, d,.
You won't get an inrush current as it's variable.
The effective is the RMS value I believe
No it won't include inrush current, it's maximum current it will draw in normal operation.
Inrush will be dealt with breaker type b, c, d,.
You won't get an inrush current as it's variable.
The effective is the RMS value I believe
I still don't understand what problem is trying to be solved by the OP.
I1Max is literally maximum current as defined by the manufacturer - so what other answer are we looking for![]()
Which standard? Which manufacturer?I asked because I would like to know the answer.
Except it isn't - it is defined by a standard to which the manufacturer must comply.
Jack
normaly they will state the full load amps you can calculate your supply cable size and breaker from that.standard breakers for domestic are b type, given the high inrush current it would require a c type
Except when it does
![]()
POWER I-TIG 200T - Everlast Europe
When it comes to DC TIG welders, you won't find a more feature packed, performance driven machine than the Power i-TIG 200T. It's user-friendly interface is thoughtfully arranged, with an intuitive design that is charachteristic that people have come to expect from Everlast products. The Power...everlastwelders.eu
----
I still don't understand what problem is trying to be solved by the OP. I1Max is literally maximum current as defined by the manufacturer - so what other answer are we looking for![]()
Which standard? Which manufacturer?
This is just becoming a circular discussion, and I'm unconvinced by "I would like to know the answer" without a "why", so I'm out. Hope you get whatever you're looking for.
Yes, thank you. It is what I quoted earlier and where I got the applicable standards from - IEC 60974 and AS 60974. It was the British version of the standard that I ended up finding.Does this BOC au leaflet help
In a nutshell, I1eff is determined from the rated input current and the duty cycle of the welding machine. It is the value used to determine the required breaker and supply cable (and power plug/socket + mains flex).
Ieff gives you the minimum size for your supply, I would still be providing your supply according to the Imax figure to give you some headroom. If you are doing a lot of full power welding it will be better for the welder
& likely give you a better duty cycle.
I'm sorry that the thread is beyond you and that you don't approve of my question. There is a lot of that on the Internet these days.I fail to see why you started this thread when you've already made up your mind. You are ignoring sound advice myself & others have given you on this thread so I see no point in continuing to post in it.
So to quote Duncan Ballantine 'I'm Oot'
The answer can be found at NEC 630.12(B)...
I1max is the maximum value of the rated supply current at maximum rated output.