All wired in, I turned it on and...
It didn't move. It made a high pitched noise, then the inverter stopped and the display now shows "E.LF". I'm trying to find the fault codes but if anyone knows what I've done wrong, please help.
Name --- Output phase loss
Description --- This function stops the inverter output if one of the three phases (U, V, W) on the inverter's output side (load side) is lost. Whether the protective function is used or not is set with Pr. 251 Output phase loss protection selection.
Check point --- Check the wiring. (Check that the motor is normal.)
--- Check that the capacity of the motor used is not smaller than that of the inverter.
Corrective action --- Wire the cables properly. y Check the Pr. 251 Output phase loss protection selection setting
There was continuity between A1 & A2, B1 & C2 and C1 & B2. I think the connections for C1 and B1 are crossed over. I think swapping them back will sort it. There was no continuity between any other ones, none to the case and all the pairs are the same resistance.I must admit I was under the impression that the size of the motor doesn't make much difference, a 2hp motor will be drawing a fraction of that 2HP with no load. I guess there could be some optimisation if max load is known but I wouldn't have thought it would stop it altogether.
You can check the motor with a meter, make sure you can see continuity between A and B, B and C and C and A. You should take the metal straps out that converts it from start to delta otherwise you will also see B to A via C when measuring A to B. Also the resistant of each winding should be similar and if you have the straps out there should be no continuity between windings. Also check they don't go to earth i.e. the casing etc.
There will be a spark along soon with better advice.
View attachment 70591
If I had a three phase mains supply, would it have this protection?The power rating won't (shouldn't!!) stop it working but it will provide protection for the motor. It prevents the drive from overloading the motor in the event of a stall or fault.