One thing I would suggest is checking the floor where it is mounted, did a 10,000KG unit for a customer last year and when we drilled a series of test holes in the floor we found it was the specified 30" at one end and less than 18" at the other.
Manufacturers specifications were a minimum thickness of 600mm (24") and the entire workshop floor nad to be torn up and relaid.
Thanks for the heads up on concrete thickness Mr Melt, this ramp will be used for transits and 7.5 tonners in a new building thats going up. I suppose I had better give its position a bit of thought and thicken up the concrete in that area.
Bob